Hi everyone just a word of caution. Installed a hard wire surge protector approximately 8 months ago and it never worked, fault E2, open ground (no ground wire connection) when ever I went to a park with power the surge protector had to be put on by pass. I left it that way till 2 days ago for the simple reason that I was boondocking. So when I went to a rv resort, I now had 50 amp service but once again had to place surge protector on by pass to have power. So contacted manufacturer of surge protector and started to do some testing and discovered that I had 68 volts between the neutral and ground which is a no no, should have reading of zero. So following the wire back to the 50 amp plug entry to the rv, so when i removed the plug the ground wire was not connected and the neutral wire was in the hole but was not tightened at all !!!!! I have had this rv since Aug. 29/24 and using full time with no ground very dangerous. I contacted Alliance immediately and they will replace 50 amp plug and new 6-3 wire. Also if I want will grant 2 hours for labour. Just a word of caution if you have a surge protector and a fault code of E2 please check the entry point into rv might be some wire not connected or loose. See pictures. One more the neutral wire has been cut at the sheating ( slit in wire, went to far into sheating)