The breaker does say dishwasher/icemaker. But I thought that was odd. I figured if the refrigerator was on, then the icemaker would be also. We do use the icemaker when we go, so I will find out in a few weeks.
M and E, what would be the best way to find this leakage. Someone earlier said to check the connections to make sure they are tight. I have not done that yet. But the washer and dryer outlets look different than most. There are no screws in the faceplate. I am certainly not an electrician, (I have been shocked numerous times doing small things at my house) so I'm not sure how to isolate the leakage.
Thanks to everyone that has commented.
I’m not an electrician either but when we were first married, we had no money so I had to learn everything (plus the basics with my dad).
Differential clamp at the panel is the best way to figure it out.
That said, I would still check the dual grounds. I don’t know enough about how the bonds park when the inverter is de-energized.
@Oregon_Camper might be able to help.
We’re headed out in a bit. I’ll look up the test and post it. It’s pretty simple with a meter.
I know the very first steps are to inspect your adapter for any bent ends. Then get a $2.00 ground tester from the hardware store and make sure the problem is not on the GFCI circuit you are plugging into is not the issue.
Power off the rig entirely.
Put your meter on ohms.
One probe on the ground at the adapter. The other on neutral.
Open or many ohms, no bond….this is what you want.
A low number of ohms, you have a dual bond and this will send some energy to ground and trip a GFCI.
This is quick and dirty…fact check it or maybe someone else can chime in with more knowledge than me.
The leakage is more challenging. It could be that you’ve already identified the source on those breakers you flipped. It could also be cumulative. That’s when it gets more challenging. I’ll find a step by step or you can google it.