32RLS Heat - Or Lack of it

dwcfish

Well-known member
After another chilly night in our 32RLS I decided to dive in and see what was going on. One thing that was immediately apparent was the mess of duct work connected to the furnace. The service manuals for the furnace as well as common sense says that you want to minimize bends in the duct work. When I got to the furnace - via the pantry - I found that there was a complete mess of bent duct work. It appears that when they installed the furnace at the factory they connected the ducts to the furnace outside of the rig and then shoved the furnace in. I have attached Pic's of before and after as well as the amount of duct work that was removed. Granted if you pull the furnace in the future you would have to access the duct work and disconnect it first. Hoping for a less chilly night tonight.............
 

Attachments

  • Lenths of Duct Work Removed.jpg
    Lenths of Duct Work Removed.jpg
    742.9 KB · Views: 92
  • Lowest Vent Duct as Originally Installed.jpg
    Lowest Vent Duct as Originally Installed.jpg
    566 KB · Views: 84
  • Middle Vent Duct as Originall Installed.jpg
    Middle Vent Duct as Originall Installed.jpg
    608.9 KB · Views: 84
  • Orginal Duct Work.jpg
    Orginal Duct Work.jpg
    543.8 KB · Views: 84
  • Re-Worked Duct Work.jpg
    Re-Worked Duct Work.jpg
    543.4 KB · Views: 84
  • Top Vent Duct as Originally Installed.jpg
    Top Vent Duct as Originally Installed.jpg
    646.5 KB · Views: 95
I’m interested to know whether the removal of the ridiculously long duct work has improved your situation.

I’m a new 32RLS owner and near the end of my New England camping season was concerned that the furnace took way too long to bring the cabin up to a comfortable 71 degrees. The kitchen island hot air register seemed to be barely blowing out hot air.

My first-year with the 32RLS camping season ended on October 31. But I wanted to use my camper for Thanksgiving as temporary living quarters while my visiting family used all the bedrooms in the house. I cranked up the furnace early in the morning, outdoor and indoor temps at about 32 degrees. It took 7 hours to bring the cabin temp to 60 degrees and it never got any warmer. And note that I only have a 15-amp receptacle for shore power at home so there was no electric heat fireplace assist.

I have an indoor/outdoor weather station installed in the camper and have a time-temp graph of that whole day. Those graphs are attached.

I’m now in the process of troubleshooting my duct work as I suspect there is something wrong with the supply to the kitchen island register. I did crawl around into the basement to look at the duct work and did see lots of extra coils and bends. But nothing like the complete mess you have.

When things warm up later this week I’ll shorten the excess duct lengths. And with the aid of a hand-held wind velocity meter, I’ll check the before/after CFM flow to the kitchen island.

I’m hoping this duct shortening will help with the cabin heating performance of my 32RLS.

My previous camper was a Grand Design 33’ fifth wheel and was able to easily and quickly heat the camper for even very cold off-season inside upgrade day-work projects. So in comparison I know the 32RLS heating system is not performing correctly.
 

Attachments

  • 6773AED6-D097-441B-8E7B-DDF2C8A788E4.png
    6773AED6-D097-441B-8E7B-DDF2C8A788E4.png
    168.6 KB · Views: 12
  • 4371BE1C-BBFE-4B62-BAAE-D0D131894A57.png
    4371BE1C-BBFE-4B62-BAAE-D0D131894A57.png
    206 KB · Views: 11

dwcfish

Well-known member
I was in the same situation with the heat at the kitchen island. Before I made the changes I would hold a Kleenex in front of the vents and they would hardly move. Since I made the changes, I can be sitting in the recliner and feel the hot air from the vent - nothing like the hot air that blows out of the bathroom vent, but it is better. When I disconnected the vents and started pulling them out it was a bit shocking, had a moment when I wondered if I would ever get to the end.

I will also note that I just had the blower fail on the heater. I am not certain, but I do wonder if all the extra duct work was putting excess strain on the blower since it could not push air through the vent. When I pulled the furnace to replace the blower I noted that there are 2 additional spots where vents could be connected on top of the furnace. I have been debating connecting an additional vent from one of these and running it under the cabinet where the coffee bar is. The question I have in doing this is how would this change the flows to the rest of the rig. Currently we have too much in the bathroom and bedroom. Big concern hear would be any reduction in air flow to the tank areas. Let me know if you have any thoughts on this. Maybe a smaller diameter vent line?

Previously we had only had rigs from Lance and heat was never an issue. We would camp a temps near zero and never had an issue.
 

CornCrib

Well-known member
One thing to consider ... if you put that additional vent under the coffee bar .... is to put a damper in each line. Then you could go down there and "tune" the airflow to get it to where you want it to be. Perform your own air balance.
 

dwcfish

Well-known member
CornPopper - I have thought about this. My concern is that when reading the service manual on the furnace you need to be careful that there is sufficient flow out of the furnace or you may have an issue with the hi limit switch going on and off. I do wonder if the duct work issue was causing some of this problem anyway and causing reduced heat output. Need an engineer to help us here...........
 

GDavis

Member
I have the same issue with my 30RLS, and also found excess duct twisted behind my furnace. After removing it the airflow to the island improved but it is still much better to the bathroom/bedroom. Would also like to know if we could use the other outlets on the furnace.
 

Ssgdoug112

New member
I have read that the center outlet on the furnace puts out the most airflow and that many have that line connected to the bathroom vent. Read that reversing them helps also.
 

Ssgdoug112

New member
After another chilly night in our 32RLS I decided to dive in and see what was going on. One thing that was immediately apparent was the mess of duct work connected to the furnace. The service manuals for the furnace as well as common sense says that you want to minimize bends in the duct work. When I got to the furnace - via the pantry - I found that there was a complete mess of bent duct work. It appears that when they installed the furnace at the factory they connected the ducts to the furnace outside of the rig and then shoved the furnace in. I have attached Pic's of before and after as well as the amount of duct work that was removed. Granted if you pull the furnace in the future you would have to access the duct work and disconnect it first. Hoping for a less chilly night tonight.............
Was it difficult to gain access to the furnace, does the wall panel come out easily, just screwed in?
 
I’m happy to report that after two trips to the dealer and direct communication with Alliance that my heating problems have been fixed.

There was excessive ducting in the underbelly leading to the kitchen island, insufficient ducted outlets to meet the Suburban specifications (3 initially installed, 4 is the minimum) and the limit switch may have been faulty.

The repair was to unravel and remove excessive ducting to the kitchen island, add a second dedicated duct to the island, add an additional duct to a new toe-kick outlet added under the coffee bar, put a restrictor on the duct to the underbelly, and replace the limit switch.

Tah dah! I’m now in Maine comfortably camping on cold nights and mornings. I’ve got four ducted outlets from the furnace now heating the cabin and one in the underbelly for sub-freezing protection.

What’s nice is that my Alliance “case manager” was talking directly to me and I was able to be a part of the process to diagnose and come up with a workable fix to the problem.
 

DanNJanice

Well-known member
I’m happy to report that after two trips to the dealer and direct communication with Alliance that my heating problems have been fixed.

There was excessive ducting in the underbelly leading to the kitchen island, insufficient ducted outlets to meet the Suburban specifications (3 initially installed, 4 is the minimum) and the limit switch may have been faulty.

The repair was to unravel and remove excessive ducting to the kitchen island, add a second dedicated duct to the island, add an additional duct to a new toe-kick outlet added under the coffee bar, put a restrictor on the duct to the underbelly, and replace the limit switch.

Tah dah! I’m now in Maine comfortably camping on cold nights and mornings. I’ve got four ducted outlets from the furnace now heating the cabin and one in the underbelly for sub-freezing protection.

What’s nice is that my Alliance “case manager” was talking directly to me and I was able to be a part of the process to diagnose and come up with a workable fix to the problem.
This seems to be a common manufacturing defect. Mine is the same, little or no flow from the island ducts. Unfortunately, my dealership is so incompetent that I wouldn't let them put a nut on a bolt, so taking it to them is out of the question. I will most likely deal with this myself.
Do you have any more details, documentation, pictures, etc about what was done?
 
This seems to be a common manufacturing defect. Mine is the same, little or no flow from the island ducts. Unfortunately, my dealership is so incompetent that I wouldn't let them put a nut on a bolt, so taking it to them is out of the question. I will most likely deal with this myself.
Do you have any more details, documentation, pictures, etc about what was done?
My RV Dealer sent me a few pics.

What they did was replace the furnace limit switch, drop the Coroplast and tidy up the existing ducts (remove excess, untwist kinks), add a second duct to the island, add a flow diverted inside the kitchen island plenum box and add a new duct and outlet box plenum with an register grill under the coffee bar tie-kick.

The heating performance is now A+.
 

Attachments

  • IMG_5505.JPG
    IMG_5505.JPG
    338.3 KB · Views: 43
  • IMG_5468.JPG
    IMG_5468.JPG
    421.4 KB · Views: 39
  • IMG_5476.JPG
    IMG_5476.JPG
    388.8 KB · Views: 39
  • IMG_5506.JPG
    IMG_5506.JPG
    372.7 KB · Views: 39
  • IMG_5508 2.JPG
    IMG_5508 2.JPG
    343.4 KB · Views: 40

DanNJanice

Well-known member
My RV Dealer sent me a few pics.

What they did was replace the furnace limit switch, drop the Coroplast and tidy up the existing ducts (remove excess, untwist kinks), add a second duct to the island, add a flow diverted inside the kitchen island plenum box and add a new duct and outlet box plenum with an register grill under the coffee bar tie-kick.

The heating performance is now A+.
Thanks for the pictures I will study them and hopefully fix it myself.
 

CharlieO

Well-known member
After another chilly night in our 32RLS I decided to dive in and see what was going on. One thing that was immediately apparent was the mess of duct work connected to the furnace. The service manuals for the furnace as well as common sense says that you want to minimize bends in the duct work. When I got to the furnace - via the pantry - I found that there was a complete mess of bent duct work. It appears that when they installed the furnace at the factory they connected the ducts to the furnace outside of the rig and then shoved the furnace in. I have attached Pic's of before and after as well as the amount of duct work that was removed. Granted if you pull the furnace in the future you would have to access the duct work and disconnect it first. Hoping for a less chilly night tonight.............
Got a question: the bottom of my 30RLS pantry is covered. Did you find an empty space there?
 
My dealer removed the bottom of the pantry cabinet and that may be sufficient to run a new duct to the furnace. They also removed the chloroplast underbelly to untangle the mess of existing duct work and to shorten the excess lengths.
 

CharlieO

Well-known member
My dealer removed the bottom of the pantry cabinet and that may be sufficient to run a new duct to the furnace. They also removed the chloroplast underbelly to untangle the mess of existing duct work and to shorten the excess lengths.
what is the purpose of sealing off that area?
 