Lost Power Kitchen AC Outlets

Dan54

Well-known member
This morning we lost power in our outlets that are located in the outside bottom of the cabinets as well as the outlet behind the TV that the TV is plugged into. The coffee maker was on & plugged into one & the toaster was plugged into the other. When the toaster lever was pushed down all 3 outlets lost power. I checked both GFCI’s & neither had tripped. I checked the circuit breakers & none had visibly tripped but I reset them all anyway. No luck. Toaster & coffee maker both unplugged. Not sure where to go from here except maybe pull the outlets out to check for damage. Suggestions?
 

Lantley

Elite Member
Do you have factory inverter set up? My TV outlet is on the inverter circuit. If you have inverter may want to check if that circuit is tripped at inverter.
 

2 Allies

Prominent Member
Sounds like the GFCI on that circuit. May want to get a meter and check the power in and out on the one feeding that circuit. On our 385FL it is on the island. When you try to reset the GFCI does the little green light come on the GFCI?
 

Dan54

Well-known member
I have the basic solar package. Don’t think I have an inverter. looked thru all my manuals & dont see an inverter manual
 

Dan54

Well-known member
Sounds like the GFCI on that circuit. May want to get a meter and check the power in and out on the one feeding that circuit. On our 385FL it is on the island. When you try to reset the GFCI does the little green light come on the GFCI?
yes the green lights are on both gfci’s. Voltage meter reads 123 volts at gfci outlets. Reset them at the outlets & breakers. No change, outlets in question still showing no voltage.
 

2 Allies

Prominent Member
Try to figure which outlet is next in the chain and start there for power in and out. May have lost a contact in the pressed conection.
Good luck Dan and keep us posted on what you find.
 

Dan54

Well-known member
I find it strange that the outlets that are nonfunctional are in the kitchen area yet are not on one of the gfci circuits. My tv is out too & is probably downstream from the outlet the toaster was plugged into. Maybe the outlet is bad. Does alliance use the cheapo rv outlets or household grade outlets? They look like the standard household type.
 

George

Prominent Member
Does alliance use the cheapo rv outlets or household grade outlets? They look like the standard household type.
In my experience with 3 diff RV's — all outlets except the GFCI are Speedwire outlets.
 

George

Prominent Member
I find it strange that the outlets that are nonfunctional are in the kitchen area yet are not on one of the gfci circuits.
On our 310RL: All the living/kitchen area outlets are wired through the island GFCI with the exception of the fireplace, dishwasher prep, and microwave. The coffee bar outlet is on the bathroom GFCI.
I color coded the outlets in the attachment — red for living/kitchen GFCI and green for bathroom GFCI.
Usually not the failure mode but maybe you have a bad GFCI? Short the conductors together to test. (e.g. Black in to Black out)
 

Attachments

  • 120vac Outlets .jpg
    120vac Outlets .jpg
    387.8 KB · Views: 21
Last edited:

Dan54

Well-known member
On our 310RL: All the living/kitchen area outlets are wired through the island GFCI with the exception of the fireplace, dishwasher prep, and microwave. The coffee bar outlet is on the bathroom GFCI.
I color coded the outlets in the attachment — red for living/kitchen GFCI and green for bathroom GFCI.
Usually not the failure mode but maybe you have a bad GFCI? Short the conductors together to test. (e.g. Black in to Black out)
So the dead outlets are all on GFCI 1 on the island. That GFCI has the green light on, shows 123 volts & the receptacle tester says it’s wired OK yet the outlets downstream are all dead. No voltage from the incoming or outgoing wires on the receptacle to the right of the range. Could the GFCI be the cause even though the green light is on, etc?
 

George

Prominent Member
So the dead outlets are all on GFCI 1 on the island. That GFCI has the green light on, shows 123 volts & the receptacle tester says it’s wired OK yet the outlets downstream are all dead. No voltage from the incoming or outgoing wires on the receptacle to the right of the range. Could the GFCI be the cause even though the green light is on, etc?
Could be. Usually not the failure mode but maybe you have a bad GFCI? Short the conductors together to test. (e.g. Black in to Black out)
Actually a less intrusive test would be to check the voltage on the GFCI OUT terminal. I forgot what they look like on the back though.
 

George

Prominent Member
...pressed in cheapo type outlet.
The part cost for a Speedwire outlet is actually more expensive than using a box and screw terminal receptacle. I guess they make up the cost with the a speedier mfg precess. 🤷🏼‍♂️ Even though you need a $500 tool to install them. Unless you use wood blocks and a c-clamp like I did one time. 😜
 

Dan54

Well-known member
Could be. Usually not the failure mode but maybe you have a bad GFCI? Short the conductors together to test. (e.g. Black in to Black out)
Actually a less intrusive test would be to check the voltage on the GFCI OUT terminal. I forgot what they look like on the back though.
So I tested GFCI by shorting the black terminals. It tripped off ok. I then tested both black terminals with the green light on. Both terminals tested positive for voltage. I then tested with the GFCI tripped & the OUT terminal had no current, only the IN terminal. So, apparently it’s not the GFCI outlet causing the problem.
 

George

Prominent Member
So I tested GFCI by shorting the black terminals. It tripped off ok. I then tested both black terminals with the green light on. Both terminals tested positive for voltage. I then tested with the GFCI tripped & the OUT terminal had no current, only the IN terminal. So, apparently it’s not the GFCI outlet causing the problem.
Disconnect the GFCI completely and wire nut the appropriate conductors together. Retest all outlets. If none are hot then I give up — except to say to follow @2 Allies advice to guess which outlet is next in the string. I would guess that the slide out outlets are not next in the chain. 🤷🏼‍♂️ Don't forget the outside outlet(s)
 

Dan54

Well-known member
Tested all GFCI 1 related outlets. Only four are affected by the outage. The two on either side of the range, the one behind the tv the tv is plugged into & the one in front of the tv by the radio tuner. When GFCI 1 is tripped all outlets are dead, not just the 4 problem outlets.
 

Dan54

Well-known member
Disconnect the GFCI completely and wire nut the appropriate conductors together. Retest all outlets. If none are hot then I give up — except to say to follow @2 Allies advice to guess which outlet is next in the string. I would guess that the slide out outlets are not next in the chain. 🤷🏼‍♂️ Don't forget the outside outlet(s)
I guess I’ll try taking out the GFCI & wiring the leads together but I’m thinking it’s a dead end since tripping the GFCI disconnects all the other outlets in the chain. Maybe pulling the dead outlets apart to check for issues would be more fruitful although maybe a broken wire somewhere?
 

George

Prominent Member
Tested all GFCI 1 related outlets. Only four are affected by the outage. The two on either side of the range, the one behind the tv the tv is plugged into & the one in front of the tv by the radio tuner. When GFCI 1 is tripped all outlets are dead, not just the 4 problem outlets.
Sorry I should have caught that in your original question. 😕 In that case I'd take down the toaster or coffee maker outlet furtherest from the TV first.
There's also the last outlet before it goes to the slide-out.
Then there will be a 120v Molex connector for slide-out removal hidden in your base cabinets somewhere.
BTW - Seems that'd be pushing an RV 15A circuit to run both. I'm pretty sure Brenda has had trouble running ANY 2 high draw appliances simultaneously.
 