SOLVED - Thermostat troubleshooting

Hemimedic37

Member
So it's November we're camping in Maryland. The temps overnight are in the 30-40s. We turned on the furnace for the first time since we've had the 370FB. The furnace ran fine for the first 10-12 hours. Woke up to a cold camper and the display on the thermostat is blank. I checked all breakers and fuses and found the 3amp fuse on the back of the thermostat blown. Moved the 3amp from a different thermostat, display is lit. Turn it to heat and about 3 seconds later it's blown again. Replace it again. I'm thinking a wire is shorted, where does the white wire go from the thermostat? Down to furnace or some where else?
 

Hemimedic37

Member
I found it! The double wire going to the furnace, I believe it had a red stripe running down the white wire was pinched under the furnace. I got it out from under and the metal on the furnace had cut the insulation on the wire causing a short. Spliced the wire where it was cut, furnace works and thermostat not blowing fuses.
 

Jim Beletti

Owner Experience Liaison
Staff member
I found it! The double wire going to the furnace, I believe it had a red stripe running down the white wire was pinched under the furnace. I got it out from under and the metal on the furnace had cut the insulation on the wire causing a short. Spliced the wire where it was cut, furnace works and thermostat not blowing fuses.

Awesome that you found that and took care of it yourself. By chance do you have a picture of the wire form when it was pinched? It could be instructive for others. Thanks for sharing!
 

marscorv

New member
So we have the same issue. I pulled the furnace out of the rig and ran a jumper wire from the Thermostat to the Furnace. Furnace works fine. Can anyone help provide thoughts on how to run a new wire? Do I need to remove all the undercarriage covering to get to the wires? Any short cuts or secrets would be most appreciated (2022 Valor 37V13)
 

marscorv

New member
So we have the same issue. I pulled the furnace out of the rig and ran a jumper wire from the Thermostat to the Furnace. Furnace works fine. Can anyone help provide thoughts on how to run a new wire? Do I need to remove all the undercarriage covering to get to the wires? Any short cuts or secrets would be most appreciated (2022 Valor 37V13)
Finally re-read the first fix and did some more investigation. When Alliance ran the thermostat wire, they wedged it behind two of the removable walls, it shorted out against the frame. replaced and functional again. Will try to attach photos.
 

Attachments

  • 20230728_124338.jpg
    20230728_124338.jpg
    894 KB · Views: 15
  • 20230728_124341.jpg
    20230728_124341.jpg
    1.1 MB · Views: 14
  • 20230728_125317.jpg
    20230728_125317.jpg
    527.6 KB · Views: 13
  • 20230728_125340.jpg
    20230728_125340.jpg
    433 KB · Views: 14
  • 20230728_125753.jpg
    20230728_125753.jpg
    592.2 KB · Views: 12
  • 20230728_134556.jpg
    20230728_134556.jpg
    133.4 KB · Views: 12
  • 20230728_134804.jpg
    20230728_134804.jpg
    153.8 KB · Views: 12
Top