We have a 2024Paradigm 340 RL. We have a private campground on the Ohio River that has 30 amp service but our service has been degraded by floods that occur on average about every 5 years. we are at the point where we need to replace the breakers & boxes because of voltage drop when multiple AC’s are running on the same leg. In order to take some of the stress off the system I’m looking at buying a portable generator that is as quiet as possible & can run at least 1 AC. Looking for info on sizing the generator output, etc. Thanks
Hi Dan, I guess it really depends on what your actual needs are.
As you know already your coach is set up for 50 amps, and you are hooked 30 amps ,so picking and choosing active loads on the system is not unfamiliar to you.
If you want to size the Gen output for your 30 amp service it would need to be at least a 3600 watt output. (120 volts x 30 amps=3600 watts).
Be careful with surge ratings and continuous output numbers, target the continuous output number within your budget.
You might also need to consider soft starts on your a/c’s(2 max. on 30 amp) if you don’t have them already, for reliable operation in summer months.
If, you don’t plan on sizing for the full 30 amps, just do the math for each load that will be running at the same time and add some cushion to handle the unexpected load and the in rush surges on heavier load devices.
Hope this helps some!